When something is wrong, the indoor display can show an error code in place of the temperature. The DIY Supplemental Manual (https://zone-air.com/manuals/ZoneAirDIYManual.pdf) says the full list is in the manual that shipped with your indoor unit (wall-mount, Airframe cassette, or Thin-Air concealed). It also calls out three codes that an installation problem often causes:

The same manual is firm about not running the system until the code is diagnosed and cleared, because forcing it can damage the compressor. Other first checks it lists: on a multi-zone, confirm every used service valve and the master valve are open, and that the head is in heat or cool, not fan-only; confirm supply voltage at the outdoor unit (it gives 110-120 VAC for 115V models and 208-253 VAC for 230V models, measured across the line terminals, not each leg to ground); and for a leaking indoor unit, confirm it is level and the drain has a continuous downward pitch.

If you smell refrigerant, hear hissing, or see oil at a fitting, the manual's leak steps are: put out ignition sources, ventilate, leave electrical switches in the affected room alone, and shut the breaker off only if the panel is outside that room, then call support or a licensed tech. Zone Air support is listed at zone-air.com/support (https://zone-air.com/support/), (801) 882-2324, Monday-Saturday 8 AM-6 PM Mountain Time.

What code or symptom did you see, and what actually cleared it?