Zone Air's current wall-mounted single-zone systems, sold under the DIY name, come in a few sizes and two voltages. Here is what the official product and spec-sheet pages actually list, so you can match a unit to the room and the circuit you have.
- 9,000 BTU wall mounts, listed for up to about 450 sq ft, in 115V (23 SEER2) and 208-230V (24 SEER2).
- 12,000 BTU wall mounts, listed for up to about 600 sq ft, in the same two voltages and SEER2 figures.
- 18,000 BTU wall mounts, listed for up to about 900 sq ft, in 208-230V only (23 SEER2).
The official FAQ is blunt about the electrical choice. Use 115V when a 9K or 12K is the right size and you do not already have a dedicated 230V circuit nearby. There is no 115V option at 18,000 BTU, and the multi-zone outdoor units are 230V as well. The spec-sheets table lists a 15A single-pole breaker for the 115V wall mounts, a 15A double-pole breaker for the 9K and 12K 230V wall mounts, and a 30A double-pole breaker for the 18K.
Those square-foot figures are the maker's coverage claims, not a substitute for a load calculation. A west-facing room with a lot of glass, or a poorly insulated space, can need more than the "up to" number suggests. Check heating too: every current model on the official spec-sheets table is listed as heating to -13°F, but output drops in extreme cold.
Line-voltage work should follow the National Electrical Code (or the Canadian Electrical Code) and your local rules. Many places require a licensed electrician and a permit. The official FAQ also says not to run a 115V unit on an extension cord.
Which wall-mount size and voltage did you end up with, and did the existing circuit decide it for you?