Official Zone Air pages currently list 2-zone and 3-zone systems, with one outdoor condenser serving two or three indoor units. You can buy matching wall-mount, Airframe cassette, or Thin-Air concealed bundles, and the build-your-own page says you can mix those indoor types on one condenser.
A detail that is easy to miss is on the spec sheets (https://zone-air.com/spec-sheets/) page: the BTU figure in a multi-zone product name is the indoor heads added together, not the size of the outdoor unit. The same page says every current Zone Air multi-zone system uses one 27,000 BTU/h condenser, which is allowed to connect up to 36,000 BTU/h of indoor capacity, so a connected total above 27,000 is expected.
The DIY Supplemental Manual (https://zone-air.com/manuals/ZoneAirDIYManual.pdf) is the one to read before you power a multi-zone system up:
- Each indoor unit gets its own pre-charged line set and its own communication cable, both landed on the same lettered port (A, B, or C).
- Label both ends of every line set and cable as you go, or a swapped zone is miserable to untangle later.
- Unused ports must stay capped and closed. The manual warns that an open unused port can vent the entire charge.
- Before the first start, open the service valves on every connected zone, plus the master valve above them. Leave the valves on an unused, capped port closed. Running the system with a used valve still shut can damage the compressor.
The official FAQ also notes that a single-zone outdoor unit cannot be converted later. If a second room is likely, that is a reason to start with a multi-zone condenser.
If you have a 2-zone or 3-zone system, how did you split the rooms, and did you mix indoor types?