Most Zone Air installs are built around a factory-sealed, pre-charged R-454B quick-connect line set. The official FAQ says a 16 ft set is included with single-zone wall mounts, and other systems take one pre-charged set per zone. The DIY supplement says those sets are offered from 5 to 75 ft. The important rule in that manual is not to stretch, splice, cut, or extend a pre-charged set. Measure the real route, including rise and bends, before you order.
9K/12K and 18K systems use different line sizes, so use the set listed for your capacity. Zone Air also sells empty standard-flare line sets. Those are not pre-charged; the official sheet for that style says a vacuum pump and EPA certification are required. Do not mix the two up.
The DIY manual's torque table for the quick-connect couplings is:
- 1/4 in and 3/8 in: 18 to 20 lb-ft
- 1/2 in: 30 to 35 lb-ft
- Larger couplings have their own higher figures in the same table
After the valves are open, leak-check every joint (a soapy solution is the method in the troubleshooting section) before you wrap or cover them. If a joint still bubbles, the manual says not to take the fitting apart; call support. Refrigerant service is licensed work.
On the electrical side, line power lands at the outdoor unit only. A 4-conductor cable (terminals 1, 2, 3, and ground) feeds the indoor unit. The official spec-sheets table lists a 15A single-pole breaker for 115V 9K and 12K wall mounts, 15A double-pole for the smaller 230V single-zone units, and 30A double-pole for 18K wall mounts and the multi-zone condensers. Always confirm against your unit's rating label. The DIY manual describes an optional 115V pigtail for the 9K and 12K wall mounts into a dedicated outdoor-rated outlet; the FAQ says never use an extension cord. Have a licensed electrician do the line-voltage work and pull any required permit.
What line-set length did you actually need, and did the circuit already exist or did you add one?